Floor and Subfloor Installation Over Concrete Q&A
Be sure to scroll down... there may be more than one question on this page!
Dear NH,
What is the best way to install a plywood subfloor over concrete slab?
Regular or treated plywood? Glued or nailed? Plastic for vapor barrier between
plywood and slab?
LM from Hot Springs, AR
I don't think it is a good idea to install raw plywood directly over a slab
if avoidable. It is too hard to attach securely and does not allow you to
install insulation or a vapor barrier underneath.
Instead, you should install strips of wood on the slab as nailers, 2x4's. You
can use them laid on their side to give less of a rise, or even use 1x2's. These
nailers should be spaced no more than 16" apart as with a standard floor.
They should be nailed and glued with construction adhesive to be sure they will
not loosen later.
You can install a foam board as a weatherstrip between the nailers. A vapor
barrier is also advisable. A heavy construction grade plastic tarp can be laid
on the floor before the nailers are installed.
The most important consideration is whether or not you get water in this
area! You also didn't mention whether or not your slab is below grade, such as
in a basement. If there is a history of water problems, I advise you to either
eliminate the water problem completely before considering any renovation like
this, or instead go with carpet placed directly on the slab (or with padding).
Water under a raised floor can be a real problem... virtually impossible to dry
out and a real mildew magnet!
Dear NH,
We have recently converted 1/2 of our garage into an extra bedroom. We
live in Massachusetts where we have a cold winter climate. The garage floor is a
concrete slab on grade. Needless to say our heating bill for the winter was very
high. The walls and roof have been insulated with fiberglass batt insulation and
we are in the process of insulating the floor.
We are planning to lay 2x4's on their sides, 24 inches on center. Then we are
laying 2 ft x 8 ft x 2 inch thick rigid insulation sheets between the 2x4's.
Then we are applying a 6 mil polyethylene vapor barrier over the entire area
which will be covered by 3/4 inch plywood underlayment, a carpet pad and
carpeting. We are also considering topping off the rigid insulation (about 1-1/2
inches) with loose fill insulation as normally used in attics. Is this a good
method of reducing heat loss through the floor? Should the vapor barrier be
above the insulation or below on the concrete slab? Any other suggestions?
BS from Tewksbury, MA
BS,
Sounds like a good plan! I do have a couple of suggestions. First, there is
no reason to use 2x4's. 2x3's are plenty adequate. Some folks even use 1x2's, though I like the
increased rigidity of the 2x3's and the extra space for insulation, You should
nail them to the floor (every three or four feet is plenty) with a power nailer
so everything stays put! This will insure that the floor will not do anything
surprising over time. Oh... be sure that the lumber you use is straight and has
been acclimated to room temperature for at least a few days or longer to
minimize warping and shrinkage. Don't under any circumstances use wet wood...
you'll be sorry!
Though 24" on center is acceptable from a load standpoint… obviously
the 2x3's will not sag since they are on the slab… using a 16" on center
installation will give you a more rigid floor surface.
The vapor barrier should be right on the concrete. If you sandwich wood
between the vapor barrier and the concrete, it will absorb moisture and
eventually begin to rot… big time trouble!! It is better that the wood be
allowed to breathe and reach a normal room moisture level.
As far as laying extra loose insulation upon the rigid insulation, my
question to you is... why?? Once the oak floor is installed and the slab is
essentially sealed under the floor, it is no longer cooled by the outside. The
extra insulation will only give mice a great nesting place. If you feel the urge
to add more insulation anyway, use additional rigid insulation instead.
As an aside, you should check with your building inspector to see if you can
legally run electrical wiring under the floor. If you don't have another
convenient way to run the wires, this might be a helpful timesaver.
NH
Return to NH's Question and Answer Index
|